michael333
Mechanical
- Jun 15, 2007
- 20
To Everyone,
I have a design where I'm using 2 inline centrifugal fans (each fan is Cook: Model GN-740) in a pull-pull arrangement for crossing airstreams via a static plate heat exchanger (Renewaire: Model CA2X). EF-3 exhausts air from public restrooms and a janitor's closet via the CA2X out the bldg. and SF-1 supplies outdoor fresh air via the CA2X to individual Mitsubishi ceiling cassettes.
It's a simple straight-forward design. Systems are installed.
EF-3 design = 525 CFM @ 0.75 ESP and SF-1 design = 500 CFM @ 0.875 ESP. Specified variable-speed controller for each fan.
Cook cutsheets and literature state the GN-740 can do ~500 CFM @ .875 ESP, 398 Watts, 1600 RPM.
I get a TAB report that states the following:
EF-3 = 374 CFM @ 0.24 in wc ESP actual, 1 amp. Fan is 29% low on airflow. Motor FLA = 2 amps.
SF-1 = 136 CFM @ 0.08 in wc ESP actual, 1 amp. Fan is 72% low on airflow. Motor FLA = 2 amps.
Direct Drive motor is on high speed for each fan according to the TAB report.
Do not know the actual RPM, only the actual amps.
I'm baffled at the low airflow CFM of these fans at such a low ESP.
EF-3 should be ~795 CFM @ 0.24 ESP according to Cook's literature.
SF-1 should be ~850 CFM @ 0.08 ESP according to their literature.
I and another colleague visited the job site and verified the following regarding both these systems:
-Inlet and outlet ductwork to each inline fan is good. No reason for system effect to cause the poor performance.
-Traverses were taken at fairly good locations in each system.
-Suction and discharge statics taken at good locations
-Variable speed controller wired up correctly, per Cook's installation manual, for each fan.
-Fans are on high speed
-We concluded that the fan wheels must be rotating in the correct direction because they're single-phase inline from the factory.
we did not physically check the fan rotation based on the above assumption.
-filters are in the correct location in the CA2X per the installation manual
-filters on the outside air inlet side of the CA2X were fairly dirty, but not that bad.
-airstreams cross correctly in the CA2X per the install manual
-turning vanes were installed in all 90 deg elbows of the ductwork
I'm even more baffled after my jobsite visit.
I'd welcome anyone's responses/advice for the following questions:
Why are these fans performing so low a airflow at a low ESP?? I'd expect to see a high ESP @ such low airflows!
Has anyone out there ran into issues with Cook's inline fans (GN-740) not performing according to their literature??
Is it possible that the fan rotation is in the wrong direction, even if they're single-phase from the factory??
Possible something is blocking airflow within the fan and motor housing itself?
Is it possible that both these fans came from a bad lot from the factory??
I'm going to put this issue back in the mech contractor's lap so that he and Cook can figure out why these fans are not performing.
Is this a good course of action??
Thank you for any advice that someone may afford on this,
Mike V P.E., CxA
I have a design where I'm using 2 inline centrifugal fans (each fan is Cook: Model GN-740) in a pull-pull arrangement for crossing airstreams via a static plate heat exchanger (Renewaire: Model CA2X). EF-3 exhausts air from public restrooms and a janitor's closet via the CA2X out the bldg. and SF-1 supplies outdoor fresh air via the CA2X to individual Mitsubishi ceiling cassettes.
It's a simple straight-forward design. Systems are installed.
EF-3 design = 525 CFM @ 0.75 ESP and SF-1 design = 500 CFM @ 0.875 ESP. Specified variable-speed controller for each fan.
Cook cutsheets and literature state the GN-740 can do ~500 CFM @ .875 ESP, 398 Watts, 1600 RPM.
I get a TAB report that states the following:
EF-3 = 374 CFM @ 0.24 in wc ESP actual, 1 amp. Fan is 29% low on airflow. Motor FLA = 2 amps.
SF-1 = 136 CFM @ 0.08 in wc ESP actual, 1 amp. Fan is 72% low on airflow. Motor FLA = 2 amps.
Direct Drive motor is on high speed for each fan according to the TAB report.
Do not know the actual RPM, only the actual amps.
I'm baffled at the low airflow CFM of these fans at such a low ESP.
EF-3 should be ~795 CFM @ 0.24 ESP according to Cook's literature.
SF-1 should be ~850 CFM @ 0.08 ESP according to their literature.
I and another colleague visited the job site and verified the following regarding both these systems:
-Inlet and outlet ductwork to each inline fan is good. No reason for system effect to cause the poor performance.
-Traverses were taken at fairly good locations in each system.
-Suction and discharge statics taken at good locations
-Variable speed controller wired up correctly, per Cook's installation manual, for each fan.
-Fans are on high speed
-We concluded that the fan wheels must be rotating in the correct direction because they're single-phase inline from the factory.
we did not physically check the fan rotation based on the above assumption.
-filters are in the correct location in the CA2X per the installation manual
-filters on the outside air inlet side of the CA2X were fairly dirty, but not that bad.
-airstreams cross correctly in the CA2X per the install manual
-turning vanes were installed in all 90 deg elbows of the ductwork
I'm even more baffled after my jobsite visit.
I'd welcome anyone's responses/advice for the following questions:
Why are these fans performing so low a airflow at a low ESP?? I'd expect to see a high ESP @ such low airflows!
Has anyone out there ran into issues with Cook's inline fans (GN-740) not performing according to their literature??
Is it possible that the fan rotation is in the wrong direction, even if they're single-phase from the factory??
Possible something is blocking airflow within the fan and motor housing itself?
Is it possible that both these fans came from a bad lot from the factory??
I'm going to put this issue back in the mech contractor's lap so that he and Cook can figure out why these fans are not performing.
Is this a good course of action??
Thank you for any advice that someone may afford on this,
Mike V P.E., CxA