A combination motor starter includes an instantaneous-only breaker and a starter which starts/stops and provides overload protection.
I am looking at NEC 1999 (the latest version I have handy).
430-52.(c)(1) states the breaker should be set to 800%.
430-52.(c)(3) exception 1 states where the setting specified (800%) is not sufficient to start the motor, the setting may be increased but shall in no case exceed 1300% (excluding energy efficient motors which can go higher).
Question 1: What is the reason for the 1300% limit? It seems this may not be sufficient if the motor has kva code G, H or higher... and does not allow much margin for variability in the breaker trip point.
Question 2: I am looking at a 60hp motor. The nameplate FLA is 65.7A. The NEC table 430-150 FLA is 77A. That is a pretty big difference and it makes a big difference which value we choose as FLA in our 1300%*FLA calucaltion. Applying the 1300% to a higher number will give a higher setting. 430-6(a) states "For general motor applications, current ratings shall be determined based on (1) and (2). (1) Table Values - The values given in Tables 430-147 thru 430-150 shall be used to determine the ampacityh of conductors or ampere ratings of switches, branch short circuit and ground fault protection, instead of the actual current rating marked on the motor nameplate. (2) Nameplate Values - Separate Motor overload protection shall be based on the motor nameplate current rating".
Am I reading it correctly that I use the motor nameplate (65.7A) for the overload, but the table value (77A) for the breaker setpoint (up to 1300% * 77A) ?
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
I am looking at NEC 1999 (the latest version I have handy).
430-52.(c)(1) states the breaker should be set to 800%.
430-52.(c)(3) exception 1 states where the setting specified (800%) is not sufficient to start the motor, the setting may be increased but shall in no case exceed 1300% (excluding energy efficient motors which can go higher).
Question 1: What is the reason for the 1300% limit? It seems this may not be sufficient if the motor has kva code G, H or higher... and does not allow much margin for variability in the breaker trip point.
Question 2: I am looking at a 60hp motor. The nameplate FLA is 65.7A. The NEC table 430-150 FLA is 77A. That is a pretty big difference and it makes a big difference which value we choose as FLA in our 1300%*FLA calucaltion. Applying the 1300% to a higher number will give a higher setting. 430-6(a) states "For general motor applications, current ratings shall be determined based on (1) and (2). (1) Table Values - The values given in Tables 430-147 thru 430-150 shall be used to determine the ampacityh of conductors or ampere ratings of switches, branch short circuit and ground fault protection, instead of the actual current rating marked on the motor nameplate. (2) Nameplate Values - Separate Motor overload protection shall be based on the motor nameplate current rating".
Am I reading it correctly that I use the motor nameplate (65.7A) for the overload, but the table value (77A) for the breaker setpoint (up to 1300% * 77A) ?
=====================================