I was curious to hear from others what their philosophy was for setting instantaneous protection (50) on relays protecting MV transformer radial feeders in industrial applications.
I have always understood the approach to be to set the transformer feeders primary relay instantaneous setting above the maximum let-through fault current on the secondary of the transformer (with multiplier to account for asymmetrical offset and additional margin) in order to ensure that the primary relay does not pickup for faults on the secondary of the transformer for coordination purposes.
I have recently heard some others suggest that the this philosophy mentioned above was more of an approach with old electromechanical relays that could not have a time delay associated with the INST setting, and that with the advent of electrical relays with available INST delay, the INST setting should be set to see faults on the secondary of the transformer with a time delay to coordination with feeder breakers.
With electronic relays is it preferable to set the INST setting to be able to pickup for faults on the secondary of transformer while still maintaining coordination with using delay on setting to coordinate with feeders? By putting an delay on this INST setting is the protection of the transformer itself being compromised by delaying INST setting for internal transformer faults?
This question mainly pertains to transformers without differential protection but I'm also curious to hear approach when diff protection is present.
I have always understood the approach to be to set the transformer feeders primary relay instantaneous setting above the maximum let-through fault current on the secondary of the transformer (with multiplier to account for asymmetrical offset and additional margin) in order to ensure that the primary relay does not pickup for faults on the secondary of the transformer for coordination purposes.
I have recently heard some others suggest that the this philosophy mentioned above was more of an approach with old electromechanical relays that could not have a time delay associated with the INST setting, and that with the advent of electrical relays with available INST delay, the INST setting should be set to see faults on the secondary of the transformer with a time delay to coordination with feeder breakers.
With electronic relays is it preferable to set the INST setting to be able to pickup for faults on the secondary of transformer while still maintaining coordination with using delay on setting to coordinate with feeders? By putting an delay on this INST setting is the protection of the transformer itself being compromised by delaying INST setting for internal transformer faults?
This question mainly pertains to transformers without differential protection but I'm also curious to hear approach when diff protection is present.