I am working as a comissioning engineer i am seeking the right solution for a pipe 42 " carrying a steam media and i have a 4" control valve to control the pressure on pipe,which type of control i should use P,PD,PID OR PI?

so please guide me about this issue.
 
Replies continue below

Recommended for you

PI should be just fine.

There are lots of articles on the web about PID control.

P provides a proportional response to the difference between the setpoint and measured value. Proportional only does not bring the measurement back to setpoint.

I applies an integral function that ramps the controller output as long as the error exists.

D provides a derivative spike upon detecting the error. This is useful for slow response such as temperature loops from a heater where you adjust the fuel. The spike helps to get the change moving and is normally applied in addition to the P and I functions.

Tuning the PI loop requires a longer response.
 
a question for JLSeagull
in case of regulating the level in a scrubber(control valve after the pump) should we use PI or PID?
NB
scrubber--> pumps(export condensate)--> control valve
 