djr3203
Electrical
- Aug 3, 2011
- 57
I just ran by an issue where I have a 3phase, 100A disconnect feeding (2) 3phase, 50A disconnects that serve electric space heaters. The load side of the disconnect has (3) #2AWG feeding into a wire gutter where Polaris splices were used to splice down to (2) 50A feeders at #8AWG each going to their respective conduit and disconnect within 10' of the splice.
The splice kit on all three phases has overheated and broken down the insulation of the wires and splice. I measured the amps on all three phases and I was reading from 69A-72A on each phase, well within the ampacity of the wires. The splice blocks were stacked pretty close together.
Could the overheating be due to the proximity of the splices to each other? All the connections appear to be good, so I don't think it is from a bad connection.
Could the heating be associated with inductive heating? I thought the closer the phase conductors are the better it is to limit inductive heating?
DJR
The splice kit on all three phases has overheated and broken down the insulation of the wires and splice. I measured the amps on all three phases and I was reading from 69A-72A on each phase, well within the ampacity of the wires. The splice blocks were stacked pretty close together.
Could the overheating be due to the proximity of the splices to each other? All the connections appear to be good, so I don't think it is from a bad connection.
Could the heating be associated with inductive heating? I thought the closer the phase conductors are the better it is to limit inductive heating?
DJR