martinrelayer

Electrical
Oct 26, 2007
68
Hi all,

we are thinking if there's some insulation monitor for cables.
They carry 230Vac, that are for a contact of safety switch in field.
The cable construction is with armour.

thanks in advance!!!!
 
Replies continue below

Recommended for you

one more thing is that those 230Vac are Live and Neutral.
i've seen insulation monitors for ungrounded systems but this is not the case..
 
If it is a system with an earthed neutral then you might find it better to look at residual current detection, for example this type of device:
Bender also make insulation monitoring equipment for non-earthed systems, I just don't think that's what you need in this application. Give them a ring, they're quite knowledgeable.
 