I am currently reviewing a new transformer control panel drawing and was curious which of the integral transformer protection functions are typically used for alarming and which ones are used for tripping upstream protection. Looking at the control drawings the following protective functions are supplied with the transformer and are avaliable with NO and NC contacts:
26Q1 - Top Oil Temp Alarm (60deg C)
26Q2 - Top Oil Temp Alarm (90deg C)
71Q1 - Liquid Level Low
63P - Pressure Relief Tank
63VP-V - 3.5 Vacuum Alarm
63VP-P - 7.0 Pressure Alarm
63 - Rapid Pressure Rise Relay Tank
For this application the transformer is protected on the primary by a fused switch as well as an upstream 13.2kV breaker that is dedicated for the transformer feed. The customer has stated that he only wants the 63 (Rapid Rise Relay) to trip the upstream breaker through an 86 and just simply alarm back to SCADA for the rest of the elements.
I'm curious to hear from others if this is typical, or if other elements besides the 63 are typically used to trip upstream protection.
Thanks
26Q1 - Top Oil Temp Alarm (60deg C)
26Q2 - Top Oil Temp Alarm (90deg C)
71Q1 - Liquid Level Low
63P - Pressure Relief Tank
63VP-V - 3.5 Vacuum Alarm
63VP-P - 7.0 Pressure Alarm
63 - Rapid Pressure Rise Relay Tank
For this application the transformer is protected on the primary by a fused switch as well as an upstream 13.2kV breaker that is dedicated for the transformer feed. The customer has stated that he only wants the 63 (Rapid Rise Relay) to trip the upstream breaker through an 86 and just simply alarm back to SCADA for the rest of the elements.
I'm curious to hear from others if this is typical, or if other elements besides the 63 are typically used to trip upstream protection.
Thanks