Our design contractor is presently designing an 11kV double-ended substation with normally closed bus tie and supplied to two separate feeders from another 11kV substation (no transformers in between). As a standard protection scheme, our design contractor provided directional phase and ground overcurrent relays on both downstream 11kV incomers + a non-directional phase and ground overcurrent relays. In the upstream 11kV feeeders, non-directional phase and ground overcurrent relays where also provided. In addition, a pilot wire type (line Differential) unit protection is provided. The protection scheme is also provided with inter-tripping schemes (mutual trip of upstream and downtream breakers) on both directional and non-directional schemes.
Now, our client advised as to remove the inter-tripping schemes since directional and pilot wire type unit protection is provided which I disagree. For an incoming line cable fault, inter-trip between upstream and downtsream breakers is a must. Can anyone provide me with more second opinions to back me up.
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
Now, our client advised as to remove the inter-tripping schemes since directional and pilot wire type unit protection is provided which I disagree. For an incoming line cable fault, inter-trip between upstream and downtsream breakers is a must. Can anyone provide me with more second opinions to back me up.