Interchanging phases and neutral of a 3 phase transformer LV secondary 3

Status
Not open for further replies.

edison123

Electrical
Oct 23, 2002
4,463
A 11 KV / 415 V, 1600 KVA, Dyn11 transformer nameplate and secondary terminals.

Nameplate

Nameplate_tkqt95.jpg



Original – neutral at bottom and phases at top

Neutral_at_bottom_rb5hrz.jpg



Proposed – neutral at top and phases at bottom

Neutral_at_top_srzjfy.jpg



Will this interchange of phases and neutral change the transformer characteristics in any way, like phase angle, polarity etc.?

This is a Dyn11 transformer. If I interchange the phase and neutral as above, will the phase angle change, for example to Dyn1?

Thanks in advance for your tips.


Muthu
 
Replies continue below

Recommended for you

It will become Dy5 vector group +positive polarity. But if you are working in isolated mode it may not create problem. Check the live clearances from bottom connections to ground.
 
Vector group shows the relative position of LV phase voltage with respect to HV phase voltage. The voltage vector changes from 11 o'clock position to 5 o'clock position when you interchange line and neutral.
 
Yes, It is possible to swap the connection of the neutral and the phase conductors converting the connection from Dyn11 to Dyn5 as mentioned by prc in the post above.
We should be aware that both connections have 1800 apart (+300 & -1500). Therefore, make sure if there is the intention of paralleling two systems the phase displacement should be identical. Also if the changes are implemented, the relay and CT polarities should be reviewed.
By visual inspection, it appears that the phase to ground clearances are OK in both cases as indicated in the illustration below. Also, the physical view, connection diagrams, and phase-shifting vector group is shown as a result of swapping the neutral with the phases.

.....
Transformer_Convertion_Dyn11_to_Dyn5_zu4ryb.jpg
 
Thanks, prc.

Thanks, cuky2000 for the great illustration.

Since this is not operated in isolated mode, I have decided to keep the original connections.

Muthu
 