Eleanor White
Electrical
- Jan 31, 2021
- 20
Heard this from an engineer who worked on a
rural diesel generator system feeding an
18-mile, 12.5 kv distribution line.
The line had two sets of main line fused
disconnects out on the main line, some miles
from the generating station.
(Pretty much all of the load was domestic, in
a couple of small villages, with a few small
motels and shops. No industry.)
The diesels were three 800 kw units, with
two units paralleled much of the day, and some
of the night. These were 600 volt units.
An experiment was scheduled to see what sort
of fault current was available at the diesel
station, so as to review the fuse coordination
scheme.
At the scheduled time (middle of the night,)
the disconnects at the power plant were opened,
and a disconnect with a test fuse, one side
grounded, was closed in on the unloaded
generators. (Using the station's 600 volt
main breaker.)
The first test used a 7 amp fuse, rather light.
The 7 amp fuse did NOT blow, instead, the
600 volt side breakers on the generators tripped.
The experiment was cancelled as it was clear that
the short circuit current situation was far
different from distribution lines fed by large
transmission lines.
What is very interesting is that the disconnects
out on the line had 80 amp fuses closer to the
station, followed by 50 amp fuses further out.
Line crews reported that indeed, the 80 and 50
amp fuses had indeed blown during various storm
activity, yet, the diesels could not blow a
7 amp fuse right outside the station.
My estimate is that the impedance of the line
between the station and the mid-line fuses allowed
the generators to not drop their voltage, which
made it possible to more slowly melt a heavy
fuse.
So effective short circuit current was very low
at the station, and actually ROSE with distance
from the station.
Live and learn?
Eleanor White
rural diesel generator system feeding an
18-mile, 12.5 kv distribution line.
The line had two sets of main line fused
disconnects out on the main line, some miles
from the generating station.
(Pretty much all of the load was domestic, in
a couple of small villages, with a few small
motels and shops. No industry.)
The diesels were three 800 kw units, with
two units paralleled much of the day, and some
of the night. These were 600 volt units.
An experiment was scheduled to see what sort
of fault current was available at the diesel
station, so as to review the fuse coordination
scheme.
At the scheduled time (middle of the night,)
the disconnects at the power plant were opened,
and a disconnect with a test fuse, one side
grounded, was closed in on the unloaded
generators. (Using the station's 600 volt
main breaker.)
The first test used a 7 amp fuse, rather light.
The 7 amp fuse did NOT blow, instead, the
600 volt side breakers on the generators tripped.
The experiment was cancelled as it was clear that
the short circuit current situation was far
different from distribution lines fed by large
transmission lines.
What is very interesting is that the disconnects
out on the line had 80 amp fuses closer to the
station, followed by 50 amp fuses further out.
Line crews reported that indeed, the 80 and 50
amp fuses had indeed blown during various storm
activity, yet, the diesels could not blow a
7 amp fuse right outside the station.
My estimate is that the impedance of the line
between the station and the mid-line fuses allowed
the generators to not drop their voltage, which
made it possible to more slowly melt a heavy
fuse.
So effective short circuit current was very low
at the station, and actually ROSE with distance
from the station.
Live and learn?
Eleanor White