I have two sets of (8)4"C with (4) 600kcmil 3 phase 480V feeders running in a concrete encased duct bank supplying a switchgear from (2) 2000KVA transformers. The duct bank runs approx. 10 feet below a some rooms where there will be sensitive equipment for a bioengineering facility. The rooms will be constructed out of C.I.P concrete walls and floors. The client has expressed concern with interference from the duct bank.
Question:
1. Has anyone ever experienced trouble with EMI radiation from service feeders carrying this magnitude of current? If so, what was the distance from the feeders where this trouble was encountered?
2. Would the rebar reinforcement in the walls and floors of the room provide any protection from interference?
3. Does anyone know how to model the magnitude of EMI radiation off 3 phase parallel conductors?
The client is pushing for twisted feeders. My research has lead me to believe that the twisted feeders are primarily for ease in pulling the wires. I know twisted pair wires are used for signal wires to reduce common mode noise when transmitting differential signals.
Questions:
A. Would twisting the 3 phase feeders reduce the EMI radiated from the feeders?
I think the only way to truly cancel the EMI radiation would be to create an electromagnetic shield around the rooms or around the duct bank.
Questions:
B. I know an electromagnetic shield/faraday cage will cancel exterior noise from reaching the interior. Will an electromagnetic shield work in the other way and cancel the EMI radiated from the feeders outside of the shield/cage?
C. Could a wire mesh be cast in the concrete in a cage like structure around the duct bank and grounded to produce an electromagnetic shield?
Thank you for bearing with this extremely long thread. Please keep in mind that my electromagnetic theory fundamentals are quite rusty
Question:
1. Has anyone ever experienced trouble with EMI radiation from service feeders carrying this magnitude of current? If so, what was the distance from the feeders where this trouble was encountered?
2. Would the rebar reinforcement in the walls and floors of the room provide any protection from interference?
3. Does anyone know how to model the magnitude of EMI radiation off 3 phase parallel conductors?
The client is pushing for twisted feeders. My research has lead me to believe that the twisted feeders are primarily for ease in pulling the wires. I know twisted pair wires are used for signal wires to reduce common mode noise when transmitting differential signals.
Questions:
A. Would twisting the 3 phase feeders reduce the EMI radiated from the feeders?
I think the only way to truly cancel the EMI radiation would be to create an electromagnetic shield around the rooms or around the duct bank.
Questions:
B. I know an electromagnetic shield/faraday cage will cancel exterior noise from reaching the interior. Will an electromagnetic shield work in the other way and cancel the EMI radiated from the feeders outside of the shield/cage?
C. Could a wire mesh be cast in the concrete in a cage like structure around the duct bank and grounded to produce an electromagnetic shield?
Thank you for bearing with this extremely long thread. Please keep in mind that my electromagnetic theory fundamentals are quite rusty