I have a question of whether or not intermediate lateral ties are required for square foundation pedestals (30" sq. x 4' ht.). I have referenced a closed thread above because it's sort of a similar question. Our office is split on the subject - some of us feel that the true purpose for intermediate ties in columns per ACI isn't realized in the type of pedestals we usually see.
My particular footing:
24" dia. drilled pier
30"x30"x4' ht. pier cap, 18" above grade, 30" below grade
Supports a W12x65 T-post, 25 ft. tall with a fixed-base-plate(independant cantilever column).
Base Plate loads - 8 kips vertical and a 50 k ft moment.
Seismic design category C, which is due to being in a Site Class E.
Reinf. in Cap: 12-#5 Vert.@ 8" sp., #4 Ties.
Does anyone feel that ACI318 directly applies to this question? Ch.22 refers to plain concrete pedestal being allowed for Horiz/Vert ratio less than 3. So, no intermediate ties needed?
I have a question of whether or not intermediate lateral ties are required for square foundation pedestals (30" sq. x 4' ht.). I have referenced a closed thread above because it's sort of a similar question. Our office is split on the subject - some of us feel that the true purpose for intermediate ties in columns per ACI isn't realized in the type of pedestals we usually see.
My particular footing:
24" dia. drilled pier
30"x30"x4' ht. pier cap, 18" above grade, 30" below grade
Supports a W12x65 T-post, 25 ft. tall with a fixed-base-plate(independant cantilever column).
Base Plate loads - 8 kips vertical and a 50 k ft moment.
Seismic design category C, which is due to being in a Site Class E.
Reinf. in Cap: 12-#5 Vert.@ 8" sp., #4 Ties.
Does anyone feel that ACI318 directly applies to this question? Ch.22 refers to plain concrete pedestal being allowed for Horiz/Vert ratio less than 3. So, no intermediate ties needed?