genieconseil
Mechanical
- Nov 12, 2002
- 22
Hi all,
i'm a mec eng. From quebec Canada. I've a bit of a conflict with an other engineer concerning internal heat loads to condider equipment and people load.
I add a load of 2 people at 230btu/hr for a two bedroom (which i think is negligable but i add it anyway) and 600 btu/hr for various internal loads . I know that ASHRAE fundamentals ed.2001 sugests 1200btu/hr but in 2013 with the more energy efficient lighting, motors from fridges ect. My opinion is that these loads should be reduced as most of the appliances are taged energy star and thus much more efficient. Plus the use of these appliance is intermitent (random operation sequences) such that the compressor on a fridge will work +or- 25% a day same for H/W tanks ( plus they are insulated). I dissagree that these loads be taken in full consideration due to my previous comments.
The other engineer is trying to discredit my calculations with abuse on appliances loads he sugests 3200btu/hr witch also includes the heat loss of the motor (950btu/hr for a 1/2 hp motor efficient at at least 90%) of the central air handler for the central A/C system which is located in the ceiling of the bathroom??
For the rest it is fine, appart that i use HAP and they use trace and using the same data (envelope specs,orientation, shading) they come up with 19000 btu/hr sensible versus 16000 btu/hr for HAP without internal loads, i dont get that one!
Conlusion is that i come up with 24000 btu/hr total and he comes up with 32000btu/hr , again i dissagree with his results i think its over design and creat cycling and discomfort for the occupants.
I would appreciate anny constructive comments.
Thank you in advance
Genieconseil
i'm a mec eng. From quebec Canada. I've a bit of a conflict with an other engineer concerning internal heat loads to condider equipment and people load.
I add a load of 2 people at 230btu/hr for a two bedroom (which i think is negligable but i add it anyway) and 600 btu/hr for various internal loads . I know that ASHRAE fundamentals ed.2001 sugests 1200btu/hr but in 2013 with the more energy efficient lighting, motors from fridges ect. My opinion is that these loads should be reduced as most of the appliances are taged energy star and thus much more efficient. Plus the use of these appliance is intermitent (random operation sequences) such that the compressor on a fridge will work +or- 25% a day same for H/W tanks ( plus they are insulated). I dissagree that these loads be taken in full consideration due to my previous comments.
The other engineer is trying to discredit my calculations with abuse on appliances loads he sugests 3200btu/hr witch also includes the heat loss of the motor (950btu/hr for a 1/2 hp motor efficient at at least 90%) of the central air handler for the central A/C system which is located in the ceiling of the bathroom??
For the rest it is fine, appart that i use HAP and they use trace and using the same data (envelope specs,orientation, shading) they come up with 19000 btu/hr sensible versus 16000 btu/hr for HAP without internal loads, i dont get that one!
Conlusion is that i come up with 24000 btu/hr total and he comes up with 32000btu/hr , again i dissagree with his results i think its over design and creat cycling and discomfort for the occupants.
I would appreciate anny constructive comments.
Thank you in advance
Genieconseil