I have a situation where the one side of a fabric building wall is seeing suction when the exhaust fans are running. The wall seeing the suction is opposite of the exhaust fans. There is a hybrid system being used in that the supply is natural and the exhaust is mechanical. I feel like the reason why the suction is occuring is because the supply louvers are positioned parallel to 45degrees to the prevailing winds. This would cause a reduction in the CFM drawn through the free area based on 88*Cv*A*U. Cv would drop from .5 to .25. However, does this equation state still apply when you have a mechanical exhaust pulling through the air?
Here is what I have
The exhaust fans are 11,242 CFM * 2 = 22,484 CFM.
The intake louvers have a free area (A) = 7.44 sq ft * 2 = 14.88 sq ft. w/ 2500fpm/ fan
Volume of building = 524275 ft^3
Capacity = 300 people
Static pressure = .00
Based on 3 air changes - 26,213 CFM are required
Based on 25CFM per person for a gym like enviroment - 7500 CFM
If i use the 22484 cfm achived through the mechanical exhaust system and divide it by the 2500 fpm achieved through the louver intake system I would need 9sq ft of free area required. Which I have 1.6x's more. This would not cause suction on the intake wall though right?
Or do I look at it as creating a balanced system through CFM. The max achievable CFM through the louver can be 22484 with a windspeed of approximately 65mph and a min of 523 CFM with virtually no wind. As suggested above I don't know if this theroy applies when I have a mechanical exhaust system pulling through air???
I believe the exhaust fans needs to be variable speed in order to limit the CFM. Another engineer suggested a larger free area natural intake. Either or, I think that they both accomplish the same results?
Here is what I have
The exhaust fans are 11,242 CFM * 2 = 22,484 CFM.
The intake louvers have a free area (A) = 7.44 sq ft * 2 = 14.88 sq ft. w/ 2500fpm/ fan
Volume of building = 524275 ft^3
Capacity = 300 people
Static pressure = .00
Based on 3 air changes - 26,213 CFM are required
Based on 25CFM per person for a gym like enviroment - 7500 CFM
If i use the 22484 cfm achived through the mechanical exhaust system and divide it by the 2500 fpm achieved through the louver intake system I would need 9sq ft of free area required. Which I have 1.6x's more. This would not cause suction on the intake wall though right?
Or do I look at it as creating a balanced system through CFM. The max achievable CFM through the louver can be 22484 with a windspeed of approximately 65mph and a min of 523 CFM with virtually no wind. As suggested above I don't know if this theroy applies when I have a mechanical exhaust system pulling through air???
I believe the exhaust fans needs to be variable speed in order to limit the CFM. Another engineer suggested a larger free area natural intake. Either or, I think that they both accomplish the same results?