Cerkit
Electrical
- Jan 18, 2016
- 99
Hi,
I am trying to calculate what interposing CT I will require. For a delta/star transformer with the star side solidly earthed, the transformer 600MVA 22/400kV. I am proposing to have Ct ratios of 200/1 on HV side and 4000/1 on LV side assuming a 5A rated relay with the following:
HV side full load current of transformer
(600×103) / (400×√3) = 866A
CT secondary current corresponding to HV side full load current
=866/200 = 4.33A
LV side full load current of transformer
(600×103) / (22×√3) = 15745.9A
CT secondary current corresponding to LV side full load current
=15745.9/4000 = 3.94A
I am proposing to use a star/delta interposing CT on the HV side to account for the phase shift, the ratio to be (4.33A/3.94):1/√3
Please can you advise on if my approach is correct?
Thanks