Interpretation of effective wind area in ASCE7-05

Status
Not open for further replies.

mfstructural

Structural
Feb 1, 2009
230
I have a question regarding interpretation of the effective wind area used to compute wind pressure on a building. I am looking at a wall that is approximately 150' wide by 250' tall. The effective wind area for the 10% edges is going to be smaller than that for the "field" center portion of the wall. The wall consists of siding panels 12" wide with a continuous span (they span over sub-girts spaced at 4' o.c.). Regarding interpretation of the effective wind area to use on the field; do you use the total area of the field = 120'x250' = 30,000 or the tributary or effective area of each siding panel of 4'x 1' wide = 4 sq. ft? This yields a huge difference, especially at zone 5. I have attached Figure 6-17 from ASCE7-05 showing the pressure coefficient table. I also attached and excerpt from ASCE7-02 wind design guide. Questions 19 and 20 basically imply to use the smaller effective wind areas? If this is the case (especially for a masonry wall, see question 20), when would you ever have an effective wind area greater than 1000 sq ft?
 
Replies continue below

Recommended for you

The wind area depends upon the element that you are designing.

For a single screw attaching the panel to the girt, the wind area is fairly small (area trib to the single screw).

For the 12" wide panel, I'd use the 12" x 48" as the panel effective area.

For the girt, I'd use the girt span x 48".

Etc.


 