cuky2000
Electrical
- Aug 18, 2001
- 2,133
We are in process trying understanding the design parameters provided by a metropolitan utility to calculate the grounding requirement on a 138kV/13.8kV Area Substation
Some of the parameter are:
* Design LGF SC current of 46kA for 2 seconds (120 cycles) follow by 10 kA for the next second (180 cycles total)
* X/R ratio of 38.8
QUESTIONS:
1- Should we need to calculate the assymetric equivalent RMS value or are usually included in the above data?
2- There is any reference or standard that address step function as describe above?.
3- Is the energy equivalent a suitable model to determine the allowable step and touch potential based in RMS or should the peack current values play a roll in this case?
Thanks
Some of the parameter are:
* Design LGF SC current of 46kA for 2 seconds (120 cycles) follow by 10 kA for the next second (180 cycles total)
* X/R ratio of 38.8
QUESTIONS:
1- Should we need to calculate the assymetric equivalent RMS value or are usually included in the above data?
2- There is any reference or standard that address step function as describe above?.
3- Is the energy equivalent a suitable model to determine the allowable step and touch potential based in RMS or should the peack current values play a roll in this case?
Thanks