Greetings everyone,
Hope everyone is having a good day!
I had a question regarding interrupting capabilities of high voltage disconnects. Per IEEE 37.30.1, this standard provides you with the ability to conduct calculations to determine the maximum amount of capacitive and excitation/resistive currents a disconnect can break in a no-load scenario. In addition, this ties in directly to the required clearances needed for the disconnect (i.e. the more clearance you have, the higher amounts of current you can break [limits to how much current one can break are set by the standard]).
Determining the excitation/resistive current is pretty straight forward as you just take the no-load currents of your banks. Determining the capacitive currents is a bit more tricky. I have two questions:
a) the proposed disconnect installation is located immediately on the high side of the main bank. The load side of the disconnect will travel through underground cable and then transition to overhead cable before it terminates into a position in the substation. In an unloaded scenario where this disconnect is opened to provide clearance, will it see high amounts of capacitive currents due to it being interconnected to the substation where miles of transmission lines take it to the distribution substations?
b) on the high side of the main bank, we have multiple sets of CT's for protection relays and metering. I was thinking just reading the current values off the relays/metering device will tell me how much current the disconnect needs to break in an unloaded scenario. But I would like to see the current segregated into its components (capacitive vs inductance vs resistive). Is there a way I can estimate this with just the current and power factor values gotten off of these device?
Appreciate any feedback you guys can provide. Apologies if my questions don't make sense. Feel free to ask me for clarification.
Hope everyone is having a good day!
I had a question regarding interrupting capabilities of high voltage disconnects. Per IEEE 37.30.1, this standard provides you with the ability to conduct calculations to determine the maximum amount of capacitive and excitation/resistive currents a disconnect can break in a no-load scenario. In addition, this ties in directly to the required clearances needed for the disconnect (i.e. the more clearance you have, the higher amounts of current you can break [limits to how much current one can break are set by the standard]).
Determining the excitation/resistive current is pretty straight forward as you just take the no-load currents of your banks. Determining the capacitive currents is a bit more tricky. I have two questions:
a) the proposed disconnect installation is located immediately on the high side of the main bank. The load side of the disconnect will travel through underground cable and then transition to overhead cable before it terminates into a position in the substation. In an unloaded scenario where this disconnect is opened to provide clearance, will it see high amounts of capacitive currents due to it being interconnected to the substation where miles of transmission lines take it to the distribution substations?
b) on the high side of the main bank, we have multiple sets of CT's for protection relays and metering. I was thinking just reading the current values off the relays/metering device will tell me how much current the disconnect needs to break in an unloaded scenario. But I would like to see the current segregated into its components (capacitive vs inductance vs resistive). Is there a way I can estimate this with just the current and power factor values gotten off of these device?
Appreciate any feedback you guys can provide. Apologies if my questions don't make sense. Feel free to ask me for clarification.