Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Inverse Time Undervoltage Formula 3

Status
Not open for further replies.

nightfox1925

Electrical
Apr 3, 2006
567
Guys, this may be a dumb question to make but I would appreciate if you will provide me a better understanding.

A G.E. Manual states that its undervoltage delay settings defines the family of curves shown below:

T = D / [1-(V/Vpickup)]

where T = operating time
D = Undervoltage Delay Setting
(D = 0 operates instantaneously)
V = secondary voltage applied to the relay
Vpickup = Pickup Level

Looking at the sample graph, for D = 2 and %voltage pickup of 2%, the operating time is approximately 2 seconds. I'm a little confused on what values I would use for V and Vpickup to coincide with the graph below:

Inverse_time_UV_curve.jpg


My application is for a 120VAC secondary and with a target operating time of 3 seconds...what will be the Delay setting (D)?



 
Replies continue below

Recommended for you

3s at what %Vpickup? D=5 is too long, but D=1 and 2 intersect 3s at different %Vpickups. Both are faster than your target at 2%.

Since Vpickup is expressed as a percentage in the graph, V=100% (of 120V) in the formula above.
 
Hi stevenal,

Its 85% nominal volts (120VAC) for 3 seconds.

 
Depending on the relay, (you may be able to set the time dial to 1/2) I don't think that's going to happen. You would need to set the relay for a time dial of 1/2 to get a 3 second response at 85%. (85% of 120 = 102 volts. The time dial of 1 hits 3 seconds at 65% or 78 volts.
 
None of the curves shown hit that point. Shortest is D=1 at about 7s.
 
In a secondary selective switchgear, the client specs calls for 0.85P.U. U/V pickup for 2 seconds and initiate the transfer.

Is it acceptable to set a 0.85P.U. voltage pickup using a DEFINITE time of 2 seconds instead of using an inverse voltage curve?

 
IMHO - A definite time delay might be better in this application. If a momentary voltage dip occurs to say 10%V for a few cycles, do you want to transfer immediately or give the system 2 seconds to come back on its own? The inverse time curves will intitate transfer faster than the two seconds specified for low voltages.
 
Nightfox.
Pay attention on the RCWilson recommendation.
I agree 3.
Best Regards.
Slava
 
Thank you very much for all the technical assistance. We will get the settings on now.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor