Inverter connections

Status
Not open for further replies.

richerdick

Electrical
Jan 10, 2007
63
I am working on a motor gearbox assembly that is fed by a small inverter. The inverter is single phase 240v input three phase 240v output 50hz.
The motor connected to it has been connected in star or wye format.
I find this strange because the motor has two conection possibliteis 415 star or 240 wye.
To me this is wrong but there are 50-60 of these motors all connected in the same way all opperating hapily and have been for years. Could there be any reason for this connection or is it an oversite.
I started to look at this problem because the motors were stalling below 5hz changing the connection seems to help, but i dont want to create problems
 
Replies continue below

Recommended for you

Sounds like an oversight. The motor will work fine as long as the load is low. The motor will be capable of producing about 33% of rated torque connected that way.

 
Did you mean to write "415 V Delta instead of "415 V Star."
 
415 star or 240 wye.
More likely 415 V star or 240 V delta.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 