I work at a large pharmaceutical plant in the UK & we have many VSD drives on pumps, agitators & fans etc, mainly Danfoss & ABB. Both manufacturers recommend segregation of supply, motor & control cables & the use of screened motor cables to comply with EMC regulations. Our installations don’t comply with these requirements, we use XLPE SWA cable & never segregate. In two of our switch rooms from which large drives are supplied I’m unable to measure EFLI & Ip at fuse boards whilst these drives are running, my robin loop tester indicates 240V, then drops to say 40V, goes back up to 240V etc etc!!! When I press the test button to try & measure EFLI I get differing high readings (16 ohms for example!!!). With the drives off I get good readings in the region of 0.01 ohms (we have an 11KV distribution network around the site, thus the low reading). We’ve recently had some kind of EMC survey carried out on the site, the report was positive, i.e. no problems. The large drives mentioned are obviously causing disturbance in the supply.
I’d be interested to hear people’s views on this, particularly anyone genned up on EMC. If it helps, all our inverter drives are fitted with filters, although I gather the filter is pointless if the instalation is not correct.
Thanks,
Alan