Dear colleagues,
I am a little confused regarding ex-certified motors connected to an inverter of any brand. As I live in Europe, I will stick to European/IEC-terms regarding this issue, but I believe that the consequenses should be more or less the same anywhere....
As far as I understand, please do correct me if I am mistaken:
I am concentrating on equipment placed in surface areas outside mines (Group II) and areas with gases (G-group), not dust.
Zone 0 (permanent presence of explosive atmosphere):
N/A
Zone 1 (occasionally, incidental normal duty, presence):
I can use motors certified as Ex d, de, e and p.
Zone 2 (accidental, not normal duty, presence):
I can use motors certified with Ex nA or better, meaning all motors good enough for Zone 1.
So far so good, I believe I have these issues quite clear. However, the problems come when supplying these motors with an inverter. Given the certificates for the different classifications, they say that the supply should not differ from rated, nominal or tested values. So with an inverter, we have an issue....
First of all, I assume that the inverter itself is located in a non-hazardous area or a pressurized panel/cabin. Subsequently the inverter itself does not need any Ex-certification and most brands can be used. But what about the influence on the motor?
If I am correct, Ex d motors are tested with any frequency and an applicable voltage (~constant flux) within the complete range. As far as I understand, an Ex d motor can be inverter fed WITHOUT any certification on the complete package (inverter+motor)- correct??
My question is then; does all other motors (e, p, nA) have to be tested and certified by a notified body for each combination? It would not be good enough to buy any of these motors and combine with any brand of inverters without re-certification? Even if the motor-manufacturer would state that the motor is suitable for inverter-supply?
And what about the Ex de-motor, which basically is a d-motor with an e junction box? Does it have to be certified for each combination as with the other ones or does it go as a d-motor?
Appreciate your opinions on this issue. I believe it is rather tricky to get a complete overview of when a re-certification is needed or not.
Cheers!
t.
I am a little confused regarding ex-certified motors connected to an inverter of any brand. As I live in Europe, I will stick to European/IEC-terms regarding this issue, but I believe that the consequenses should be more or less the same anywhere....
As far as I understand, please do correct me if I am mistaken:
I am concentrating on equipment placed in surface areas outside mines (Group II) and areas with gases (G-group), not dust.
Zone 0 (permanent presence of explosive atmosphere):
N/A
Zone 1 (occasionally, incidental normal duty, presence):
I can use motors certified as Ex d, de, e and p.
Zone 2 (accidental, not normal duty, presence):
I can use motors certified with Ex nA or better, meaning all motors good enough for Zone 1.
So far so good, I believe I have these issues quite clear. However, the problems come when supplying these motors with an inverter. Given the certificates for the different classifications, they say that the supply should not differ from rated, nominal or tested values. So with an inverter, we have an issue....
First of all, I assume that the inverter itself is located in a non-hazardous area or a pressurized panel/cabin. Subsequently the inverter itself does not need any Ex-certification and most brands can be used. But what about the influence on the motor?
If I am correct, Ex d motors are tested with any frequency and an applicable voltage (~constant flux) within the complete range. As far as I understand, an Ex d motor can be inverter fed WITHOUT any certification on the complete package (inverter+motor)- correct??
My question is then; does all other motors (e, p, nA) have to be tested and certified by a notified body for each combination? It would not be good enough to buy any of these motors and combine with any brand of inverters without re-certification? Even if the motor-manufacturer would state that the motor is suitable for inverter-supply?
And what about the Ex de-motor, which basically is a d-motor with an e junction box? Does it have to be certified for each combination as with the other ones or does it go as a d-motor?
Appreciate your opinions on this issue. I believe it is rather tricky to get a complete overview of when a re-certification is needed or not.
Cheers!