KenAlmon
Electrical
- Apr 12, 2002
- 48
I am aware of the IP ratings of electrical or instrumentation boxes. I am also aware that in order to maintain the rating, any gland entrances have to have a similar (or higher) rating. For example, a Hawke gland with an IP66 rating can be put in an IP66 box and the rating maintained. An IP66 gland in an IP67 box would only be an IP66 box when installed.
However, I am intrigued by several rumours going around our jobsite talking about the number of threads necessary to maintain ratings. There are several cases (perhaps more) to consider:
1. a clear hole in a box will require a metric (straight) gland with an IP washer (on the outside) and serrated washer (on the inside) and tightened to some tightness.
2. an NPT threaded (tapered) hub on the box will require a minimum of five (5) turns in order to maintain the IP rating. This may or may not be at the point where the gland is tight.
3. a metric threaded (straight) hub on the box will require a minimum of eight (8) turns in order to maintain the IP rating. There may or may not be an IP washer present.
My question is whether any of this is true and whether there is a basis such as a standard that specifically identifies the number of turns etc. It would seem to me that in the case of #1 above, you would have to have it some degree of tightness. In the case of #2, I would think you would have to have the gland tight, regardless of number of threads. And in the case of #3, I would think you would have to have an IP washer and it would have to be tight in the hub, again, regardless of the number of threads.
Perhaps the confusion relates to hazardous ratings where the Canadian Rules state:
Threaded joints that are required to be explosion proof or flameproof may be threaded either tapered or straight: where tapered must be 5 fully engaged threads and where straight, must be 8 fully engaged threads.
Although you would think the hazardous rating would at least equal IP rating...
Any ideas?
However, I am intrigued by several rumours going around our jobsite talking about the number of threads necessary to maintain ratings. There are several cases (perhaps more) to consider:
1. a clear hole in a box will require a metric (straight) gland with an IP washer (on the outside) and serrated washer (on the inside) and tightened to some tightness.
2. an NPT threaded (tapered) hub on the box will require a minimum of five (5) turns in order to maintain the IP rating. This may or may not be at the point where the gland is tight.
3. a metric threaded (straight) hub on the box will require a minimum of eight (8) turns in order to maintain the IP rating. There may or may not be an IP washer present.
My question is whether any of this is true and whether there is a basis such as a standard that specifically identifies the number of turns etc. It would seem to me that in the case of #1 above, you would have to have it some degree of tightness. In the case of #2, I would think you would have to have the gland tight, regardless of number of threads. And in the case of #3, I would think you would have to have an IP washer and it would have to be tight in the hub, again, regardless of the number of threads.
Perhaps the confusion relates to hazardous ratings where the Canadian Rules state:
Threaded joints that are required to be explosion proof or flameproof may be threaded either tapered or straight: where tapered must be 5 fully engaged threads and where straight, must be 8 fully engaged threads.
Although you would think the hazardous rating would at least equal IP rating...
Any ideas?