IPC Section 504 Safety Devices (for water heaters) discrepancy

Status
Not open for further replies.

tbonebanjo

Mechanical
Nov 15, 2010
10
I was just reviewing the IPC for water heater catch pan drains and found this:
504.6(5) says the relief valve may "discharge to the floor, to the pan serving the water heater or storage tank...."
Comentary Figure 504.7(1) says "relief valve pipe terminating into a safe pan is prohibited"

Has anyone run across a formal interpretation of the allowed method? I am working on a project in DC, they do not recognize the commentary in their code, so I believe the relief valve may discharge to the pan per code. However, I seem to remember some reviewer in another location saying I had to take the relief valve to a separate receptor.
 
Replies continue below

Recommended for you

Code is minimum, but often AHJ may use their authority to require more in their area. It is up to you if you want to spend the time/effort to fight something like this.
 
The termination of T&P relief valve discharge pipes into water heater drip pans has been a long standing practice with no evidence of property damage to justify prohibition of this practice. The AHJ may use their authority to require more in their jurisdiction.

Link
 