I was just reviewing the IPC for water heater catch pan drains and found this:
504.6(5) says the relief valve may "discharge to the floor, to the pan serving the water heater or storage tank...."
Comentary Figure 504.7(1) says "relief valve pipe terminating into a safe pan is prohibited"
Has anyone run across a formal interpretation of the allowed method? I am working on a project in DC, they do not recognize the commentary in their code, so I believe the relief valve may discharge to the pan per code. However, I seem to remember some reviewer in another location saying I had to take the relief valve to a separate receptor.
504.6(5) says the relief valve may "discharge to the floor, to the pan serving the water heater or storage tank...."
Comentary Figure 504.7(1) says "relief valve pipe terminating into a safe pan is prohibited"
Has anyone run across a formal interpretation of the allowed method? I am working on a project in DC, they do not recognize the commentary in their code, so I believe the relief valve may discharge to the pan per code. However, I seem to remember some reviewer in another location saying I had to take the relief valve to a separate receptor.