AJ2002
Electrical
- Mar 4, 2002
- 27
I am working on a electrical chiller replacement job. It involves replacing an constant speed chiller with a VFD chiller. I planned on using the existing CB to feed a new harmonic filter physically inplace of the old motor starter(adjacent to existing powerpanel) and then connecting the filter to the unit mounted VFD w/CB.
An engineer says this is a violation of the NEC 25 FT Tap rule because the cables are 30 FT and a disconnect is required after the filter.
The filter consists of a two series reactors with a capacitor bank tapped after the first reactor. There is no electrical isolation, like a transformer. I am considering this filter integral to the dedicated branch circuit and not a tap rule application, therefore, no disconnect is required.
All the cabling is sized for full load. Which view correct??? Help is greatly appreciated.
An engineer says this is a violation of the NEC 25 FT Tap rule because the cables are 30 FT and a disconnect is required after the filter.
The filter consists of a two series reactors with a capacitor bank tapped after the first reactor. There is no electrical isolation, like a transformer. I am considering this filter integral to the dedicated branch circuit and not a tap rule application, therefore, no disconnect is required.
All the cabling is sized for full load. Which view correct??? Help is greatly appreciated.