I had hoped that someone had already solved this problem. Here's my design. Please help me refine it.
I've been designing a system to control ice formation, and maybe even capture some latent heat of freezing. I plan to use coils of tubing inside a barrel of antifreeze solution. The 40 F spring water is gravity fed to my site, with a static pressure of almost 50 psi. It will sustain 3.3 gpm. When cooled to 32F, this is a heat flux of about 13,000 btu/hr.
Construction: Fill a barrel with antifreeze. Immerse a copper refrigeration evaporator coil from the heat pump. Arrange the evaporator coil so that refrigerant enters the barrel at the bottom and exits at the top. Surrounding that coil in the barrel, immerse 350 feet of 1/2" pex flowing the spring water. Arrainge the pex so that the spring water enters the top of the barrel and exits out the bottom. the 350 foot length will convert the 50 psi static pressure to heat as friction loss and flow about 3.3 gpm. Control the cooling action of the evaporator coil to limit the minimum temperature of the antifreeze in the barrel to a few degrees below freezing. My hope is that some ice crystals would form in the spring pex coil, but would be swept along in the 5.5 fps flow and not buildup inside the pex.
I think that the refrigerant could be significantly below freezing and still not freeze the spring pex line.
How much freezing am I looking for? If my 2.1 kw heatpump operates at a COP of 3:1, then it will need 14,280 btu/hr from the spring water. This 14,280 btu/hr plus the 7140 btu/hr from the work of compression yields a 21,420 btu/hr system. Cooling 3.3 gpm spring water from 40 F to 32F gives 13,210 btu/hr. 1070 btu/hr would then need to be recovered from the latent heat of freezing. So about 0.4% of the spring water would need to be frozen. It seems possible. Perhaps I could use an Automatic Expansion Valve and adjust the evaporator pressure to hold the bottom part of the barrel a few degrees below freezing when it is in full-power steady-state operation. There would be no concern of freezing for less than about 1.8kw shaft input power.
Does anyone have experience with these techniques?