krisys
Electrical
- May 12, 2007
- 458
One of the motor winding temperature RTD Loop is malfunctioning and tripping. The motor is 11kV, 3300 kW, fed from 11kV switchboard.
Historically, two (2) RTDs (one from Y-phase and other from B-phase) of the same motor are out of service since commissioning. The present problem is with the second RTD of Y-phase. So now there is no RTD for Y-phase winding.
The RTD’s are connected to Areva MiCom P225 motor protection relay. The trip command is issued from MiCom relay. When the temperature trend was taken out from the DCS, most of the time the temperature is normal. However, intermittently the temperature shoots up abruptly then comes back to normal. It appears that there is something wrong with the RTD or the related circuit. Because motor temperature cannot shoot up in one winding such abruptly. Also all the other five RTDs are showing the normal temperature.
I suspect the following:
[li]EMC issues, due to which some surge is getting generated due to induction from 11kV winding[/li]
[li]Varistor (connected across the RTD for surge protection) could be malfunctioning[/li]
[li]RTD module in the motor protection relay may be having some problem[/li]
The motor is driving a very critical pump. Presently it is kept off, as Pump-B is running. But we want it to be in stand by. We are proposing to disable the RTD which is causing the motor trip and take the motor into service.
My question: Is there any risk for the motor or the pump, by disabling one RTD trip? Can other RTDs can do the job?
I would appreciate, if someone from the fraternity could share their experience.
Historically, two (2) RTDs (one from Y-phase and other from B-phase) of the same motor are out of service since commissioning. The present problem is with the second RTD of Y-phase. So now there is no RTD for Y-phase winding.
The RTD’s are connected to Areva MiCom P225 motor protection relay. The trip command is issued from MiCom relay. When the temperature trend was taken out from the DCS, most of the time the temperature is normal. However, intermittently the temperature shoots up abruptly then comes back to normal. It appears that there is something wrong with the RTD or the related circuit. Because motor temperature cannot shoot up in one winding such abruptly. Also all the other five RTDs are showing the normal temperature.
I suspect the following:
[li]EMC issues, due to which some surge is getting generated due to induction from 11kV winding[/li]
[li]Varistor (connected across the RTD for surge protection) could be malfunctioning[/li]
[li]RTD module in the motor protection relay may be having some problem[/li]
The motor is driving a very critical pump. Presently it is kept off, as Pump-B is running. But we want it to be in stand by. We are proposing to disable the RTD which is causing the motor trip and take the motor into service.
My question: Is there any risk for the motor or the pump, by disabling one RTD trip? Can other RTDs can do the job?
I would appreciate, if someone from the fraternity could share their experience.