Is NFPA #13 8.15.1.2.9 referencing a DIFFERENT type of small room?

Status
Not open for further replies.

Oremus

Mechanical
Jan 22, 2008
85
NFPA #13 2007 Ed.

8.15.1.2.9 Concealed spaces over isolated small rooms not exceeding 55 ft2 (5.1 m2) in area shall not require sprinkler protection.


"Isolated small rooms" is this meant to be a reference to the definition of a "small room" as indicated in 3.3.15 meaning it has to be light hazard etc.?

Also, does "isolated" refer to being remote or to being separated from other adjacent rooms with a fire rating?
 
Replies continue below

Recommended for you

not same as small room rule

do not have the book, but do not believe any rating is required, maybe fire blocking only?? think the idea is fire maybe will not start there, or no reason to require spinklers in the area

if you think of an area above a ceiling in a restroom, something like that small
 
Thanks CDAFD, I see someone else has to work on 'labor day' as well :)
 
another thing... you can have two such small rooms adjacent to each other right? Isolation in this sense means isolated (by a barrier)from the common attic space right?
 