jantoffman
Electrical
- Feb 20, 2008
- 6
Am I missing the boat? The problems with pump runout as I understand it, are possible overloading the motor and possible cavitation with resulting vibratation and pump damage due to excessive flow.
I'm looking at a system that will be at low head for one step in the process, and high head at the next step in the process. I want to protect the pump against runout during the short low head step in the process.
Now I've sized my motor way above the runout BHP so I shouldn't have a problem with the amps/HP.
My question goes to the other issue with runout (cavitation/vibration). If I lower the speed of the pump during the low head phase of pumping, as I understand it I effectively drop down the curve and can find a speed that hits the low head point at the flow I want. But what If I'm limited to 40% pump speed on my VFD and that still hits the low head value at the far right end of the curve?
If I'm not really moving the maximum flow rate of the pump would I still have a problem? Would efficiencies drop off so much that I still see high amps?
And lastly, can I just control the VFD to a certain # of amps to protect against runout? Is that considered runout protection? Effectively that's what I'm trying to do.
Thanks for any input.
-JT
I'm looking at a system that will be at low head for one step in the process, and high head at the next step in the process. I want to protect the pump against runout during the short low head step in the process.
Now I've sized my motor way above the runout BHP so I shouldn't have a problem with the amps/HP.
My question goes to the other issue with runout (cavitation/vibration). If I lower the speed of the pump during the low head phase of pumping, as I understand it I effectively drop down the curve and can find a speed that hits the low head point at the flow I want. But what If I'm limited to 40% pump speed on my VFD and that still hits the low head value at the far right end of the curve?
If I'm not really moving the maximum flow rate of the pump would I still have a problem? Would efficiencies drop off so much that I still see high amps?
And lastly, can I just control the VFD to a certain # of amps to protect against runout? Is that considered runout protection? Effectively that's what I'm trying to do.
Thanks for any input.
-JT