Working on a 180-ft long span PEMB and getting huge kickout loads. Geotech took "Easy Button" and used presumptive capacities from IBC Table 1806.2 for clay soils resulting in lateral resistance of 100 psf/ft depth passive and 130 psf shear strength of soil. At least they gave us 2,500 psf bearing w/ 1/3 increase. I did preliminary size based on 250 psf/ft passive for Dead + Collateral and 250x4/3 = 333 so I limited myself to 300 psf/ft for D +C +Lr
They didn't check live load reduction so we got 90-kip kickout force for Lr = 20 psf. We had them rerun with reduction and was able to drop that down to 70-kip lateral for Lr = 12 psf. I can deal with the footprint for vertical load and end up with a 12'x10' ftng so no issues there. Frost depth is 18" so the perimeter grade beam is 24" deep to give a little cushion.
CHK 1: Apply Dead load + Collateral load case and resist that with values as specified.
CHK 2: Apply D +C +Lr load case and resist with or without 1/3 increase?
CHK 3+: Use the PEMB load cases for W and E and check as normal w/ 1/3 increase or w/o increase as needed.
I gave constr team three options since the Geotech gave me less than expected lateral resistance.
► OPT 1: Step 1, drop footing from 2'-0" to 4'-0" below grade to gain passive wedge. Step 2, treat grade beams like T-Beam flanges, then drop them to bottom of footing and extend outward 8'-0" each side of the footing to gain passive wedge width. After 8'-0" taper trench back up to 24" depth. 6 x1.50' grade beam width = 9.00' so 8'-0" extension seemed reasonable. This gets me plenty of passive resistance without relying on any friction or tie backs. Original grade beams were designed as 8" wide earth formed trench (12" bucket assumed) to coincide with 8" bypass girts. I cannot get constr. team to use turn-down slab. So, I would also have to transition the grade beam trench width from 18" to 12" which I don't think will cause too much heartache w/ constr. team.
► OPT 2: Same as OPT 1 but instead of add'l excavation for the footing I would leave the footing where it is and have them trench in a key below the footing and extend that out for the grade beam. Same amount of passive wedge plus I get a little benefit from soil shear in front of key under the footing.
► OPT 3: I still want to drop the footing from 2'-0" to 4'-0" but instead of extending the grade beams out I would run a grade beam back 12' to another longitudinal grade beam forming a 'T'. Then I get soil shear for the footprint in front of the Tee plus passive on the footing and grade beam above the footing. Constr. gets to keep their 8" wide grade beam (12" bucket trench) in this case and I get a funky design utilizing the T-grade beam as a deadman. Since this approach is a little outside the norm I thought I would throw this out to you all. Would I also need to check the passive wedge in front of the T-deadman in case the failure plane is the passive wedge, or can I assume the soil mass moves laterally like on a retaining wall.
Q1) I think 12 psf Lr is a temporary load case and we should be able to use 1/3 increase for lateral and vertical bearing pressures. What say you?
Q2) Which Option would you choose and why?
They didn't check live load reduction so we got 90-kip kickout force for Lr = 20 psf. We had them rerun with reduction and was able to drop that down to 70-kip lateral for Lr = 12 psf. I can deal with the footprint for vertical load and end up with a 12'x10' ftng so no issues there. Frost depth is 18" so the perimeter grade beam is 24" deep to give a little cushion.
CHK 1: Apply Dead load + Collateral load case and resist that with values as specified.
CHK 2: Apply D +C +Lr load case and resist with or without 1/3 increase?
CHK 3+: Use the PEMB load cases for W and E and check as normal w/ 1/3 increase or w/o increase as needed.
I gave constr team three options since the Geotech gave me less than expected lateral resistance.
► OPT 1: Step 1, drop footing from 2'-0" to 4'-0" below grade to gain passive wedge. Step 2, treat grade beams like T-Beam flanges, then drop them to bottom of footing and extend outward 8'-0" each side of the footing to gain passive wedge width. After 8'-0" taper trench back up to 24" depth. 6 x1.50' grade beam width = 9.00' so 8'-0" extension seemed reasonable. This gets me plenty of passive resistance without relying on any friction or tie backs. Original grade beams were designed as 8" wide earth formed trench (12" bucket assumed) to coincide with 8" bypass girts. I cannot get constr. team to use turn-down slab. So, I would also have to transition the grade beam trench width from 18" to 12" which I don't think will cause too much heartache w/ constr. team.
► OPT 2: Same as OPT 1 but instead of add'l excavation for the footing I would leave the footing where it is and have them trench in a key below the footing and extend that out for the grade beam. Same amount of passive wedge plus I get a little benefit from soil shear in front of key under the footing.
► OPT 3: I still want to drop the footing from 2'-0" to 4'-0" but instead of extending the grade beams out I would run a grade beam back 12' to another longitudinal grade beam forming a 'T'. Then I get soil shear for the footprint in front of the Tee plus passive on the footing and grade beam above the footing. Constr. gets to keep their 8" wide grade beam (12" bucket trench) in this case and I get a funky design utilizing the T-grade beam as a deadman. Since this approach is a little outside the norm I thought I would throw this out to you all. Would I also need to check the passive wedge in front of the T-deadman in case the failure plane is the passive wedge, or can I assume the soil mass moves laterally like on a retaining wall.
Q1) I think 12 psf Lr is a temporary load case and we should be able to use 1/3 increase for lateral and vertical bearing pressures. What say you?
Q2) Which Option would you choose and why?