Aftermathematics
Electrical
- Sep 10, 2010
- 2
I am trying to size miniature circuit breakers for 1kW 3-phase motors but I'm a bit confused as to what the breaker size should be.
The motor characteristics are as follows.
Rated power=1kW
Rated Voltage=400V
Power factor=0.8
The full load current FLC was calculated using the formula; I=P/(?3*v*pf) =1.8A ? 2A
The locked rotor current(starting current) LRC= 6*flc= 12A
My question is; should the breaker be sized to the FLC of the motor or to the LRC? i.e. should the CB be 2A or 12A?
I intend to use type C circuit breakers to EN 60898 given in BS7671 but it doesn't characteristics for 2A breaker. However, ABB manufactures MCBs as low as 2A so at least I know they are available off the shelf. I understand there are MCBs specifically designed for motors. Does this apply in to the British market as well?
What is the significance of motor service factor? Does it play a role in the sizing of circuit breaker?
Please bear in mind that I'm asking from the UK hence please provide answers to British or European standards
The motor characteristics are as follows.
Rated power=1kW
Rated Voltage=400V
Power factor=0.8
The full load current FLC was calculated using the formula; I=P/(?3*v*pf) =1.8A ? 2A
The locked rotor current(starting current) LRC= 6*flc= 12A
My question is; should the breaker be sized to the FLC of the motor or to the LRC? i.e. should the CB be 2A or 12A?
I intend to use type C circuit breakers to EN 60898 given in BS7671 but it doesn't characteristics for 2A breaker. However, ABB manufactures MCBs as low as 2A so at least I know they are available off the shelf. I understand there are MCBs specifically designed for motors. Does this apply in to the British market as well?
What is the significance of motor service factor? Does it play a role in the sizing of circuit breaker?
Please bear in mind that I'm asking from the UK hence please provide answers to British or European standards