itsmoked
Electrical
- Feb 18, 2005
- 19,114
Yesterday a guy at a re-tasked cannery asked me some disturbing questions about an outlet he was trying to plug a TIG welder into. It was in a 208V setting. Seems he was getting at the outlet 120 from L1 to N and 208V from L2 to N AND 208 from L2 to the conduit! About then I told him to stay the %$#@ away from it all until I got there. I get there and the 'good Samaritan' non-electrical guy showed me the problem outlet and the subpanel where he'd just moved the white N wire to the neutral bus from the ground bus.
Turned out he'd color coded the wires starting in the outlet box according to the screws they landed on on the receptacle. I informed them that there was no ground visible and that the outlet should be L1, L2, GND not L1, L2, N. I realized they had the GND in the recep L1 and L1 in the recep GND! I re-marked the N whites to green on both ends and re-landed it on the GND bus and the recep GND. Moved the red L1 back to the recep L1 and recognizing that the recep had a big brass bar that lead down to the recep mounting screw wondered why there hadn't been an immediate breaker tripping ground-fault.
On closer inspection it was found that a rubber insulator was installed at the receptacle box AND the subpanel completely isolating the EMT from both ends thru two interposing businesses.
I removed both isolators.
Can anybody posit a rational about why this had been done decades ago "by an electrician" and then all nicely painted over?
Keith Cress
kcress -
Turned out he'd color coded the wires starting in the outlet box according to the screws they landed on on the receptacle. I informed them that there was no ground visible and that the outlet should be L1, L2, GND not L1, L2, N. I realized they had the GND in the recep L1 and L1 in the recep GND! I re-marked the N whites to green on both ends and re-landed it on the GND bus and the recep GND. Moved the red L1 back to the recep L1 and recognizing that the recep had a big brass bar that lead down to the recep mounting screw wondered why there hadn't been an immediate breaker tripping ground-fault.
On closer inspection it was found that a rubber insulator was installed at the receptacle box AND the subpanel completely isolating the EMT from both ends thru two interposing businesses.
I removed both isolators.
Can anybody posit a rational about why this had been done decades ago "by an electrician" and then all nicely painted over?
Keith Cress
kcress -