hello guys,
we are operating a 40MW captive coal power plant in order to supply our own industrial load of about 20MW. our coal plant
is connected to grid system in order to obtain a startup supply fromthe grid and to export a surplus power of about 17MW.
the grid system is very unstable. often there is under-frequency and unplanned tripping which also trips our coal plant ( mostly on under frequency of generator protection) thus tripping all our industrial load.This has become a trouble for us as steady supply to our industrial load is important.
basically i am in search for solution to following two problems:
i. Can we install a Rocof (df/dt) relay to trip the grid breakers if the grid is becoming unstable? if so, how do we determine the settings of the Rocof relay? reference to some standars/codes/literature will be appreciated.
2. will our plant operate in isolated mode once we trip the grid breakers ( a load rejection of 17MW to grid will surely cause over frequency and over voltage at our turbine and generator)? i am of the view that specific equipment ( like auto load switching units) are needed to be installed at a coal power plant to operate it in isolated mode. i will appreciate if some reference material is shared regarding isolated operation of a coal power plant of such small size ( i.e. 40MW).
regards,
we are operating a 40MW captive coal power plant in order to supply our own industrial load of about 20MW. our coal plant
is connected to grid system in order to obtain a startup supply fromthe grid and to export a surplus power of about 17MW.
the grid system is very unstable. often there is under-frequency and unplanned tripping which also trips our coal plant ( mostly on under frequency of generator protection) thus tripping all our industrial load.This has become a trouble for us as steady supply to our industrial load is important.
basically i am in search for solution to following two problems:
i. Can we install a Rocof (df/dt) relay to trip the grid breakers if the grid is becoming unstable? if so, how do we determine the settings of the Rocof relay? reference to some standars/codes/literature will be appreciated.
2. will our plant operate in isolated mode once we trip the grid breakers ( a load rejection of 17MW to grid will surely cause over frequency and over voltage at our turbine and generator)? i am of the view that specific equipment ( like auto load switching units) are needed to be installed at a coal power plant to operate it in isolated mode. i will appreciate if some reference material is shared regarding isolated operation of a coal power plant of such small size ( i.e. 40MW).
regards,