Isolation Dry-Type Transformers 3

Status
Not open for further replies.

CuriousElectron

Electrical
Jun 24, 2017
187
Hi All,
Why would we typically use an isolation transformer with the same voltage on the primary and secondary, 1:1 ratio?
Is the reason to improve the voltage regulation, maintain a robust voltage amplitude on the secondary?
What would be the other reasons?
Thanks,
EE
 
Replies continue below

Recommended for you


Please give configuration of isolation transformer, is it D-Y ?
 
An isolation transformer will degrade voltage regulation slightly.
Source regulation plus or times the isolation transformer regulation.
The transformer may be used to boost a voltage but it is then no longer a 1:1 ratio.
A 1:1 transformer may be used to develop an separately derived circuit, to suppress harmonics or to reduce arc flash, of source imedance

Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
I'm not trying to be a snot, but I might come across as one anyway...

At the risk of being obvious, an isolation transformer's raison d'être is to isolate two circuits from each other, viz., to provide a power transfer but without galvanic connection; unity ratio will be used where no change in voltage is necessary.

I said it m-y-y-y-y way . . . [ with apologies to the late Frank Sinatra ]

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
We frequently used 480 - 480/277 V transformers on large facilities where 277 V lighting was desired to isolate the lighting system ground faults and to eliminate the need to carry a large neutral throughout the 480 V system.
 
LPS to CR for using “raison d'être” in a sentence regarding engineering.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
I have used single phase 1:1 isolation transformers to deal with nuisance tripping of GFCIs. Some heating elements' insulation will degrade to the point that it will trip a GFCI at some point in its heating cycle. An isolation transformer eliminates the tripping and any shock hazard, and may be cheaper and more convenient than repeatedly replacing a heating element.
 
As dpc mentioned, isolation or unity ratio transformers are helpful in reducing the fault level in the lighting system and allow
* use of cheaper lighting distribution boards (lower fault rating) as well as
* use of MCBs in lighting and small power circuits.
These are Dyn connected and single phase load on secondary appears as phase-to-phase load on primary system thus reducing the load unbalance in the plant main distribution system.
 
LPS to CR for using “raison d'être” in a sentence regarding engineering.

C'est apropos, n'est pas?

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 