a10jp
Electrical
- May 18, 2005
- 150
In one of our facilities, we are serving the IM server room via an isolation transformer, which according to the are supplied with a separate ground, different from the distribution panel.
Is this called an isolated ground, where it is a separate ground path fed directly from the substation grounding?
Similarly, on both the standby power panel and the distribution panel, the TVSS are also to be connected to the common substation ground, which would satisfy the code of a bonded system for this facility. I confirmed with the designer, and he stated that this separate ground are to be fed from the substation ground, which confirm my understanding where the ground should be connected to.
However in Japan, grounding system are very different. Everything has a separate ground, meaning each a separate path to the ground via a ground electrode.
Had a discussion on this subject with a Japanese engineer, and he explained that the best method to comply with the code is for each of these separate system with separate grounding to be bonded at a common ground terminal. Sort of like you ground every individual system to a common ground terminal (the substation ground). Does it sound correct?
The contractor stated that the TVSS should NOT be connected to the substation ground, since it is a surge path, and it should be kept separate fromm the normal system ground. He stated the same thing for the isolation transformer for the IM room, which he said should have independent grounding, and not to the bldg substation.
I do not believe this satisfy the code, doesn't that make the bldg have different ground potential, at the normal substatsion ground, isolation transformer, TVSS?
Is this called an isolated ground, where it is a separate ground path fed directly from the substation grounding?
Similarly, on both the standby power panel and the distribution panel, the TVSS are also to be connected to the common substation ground, which would satisfy the code of a bonded system for this facility. I confirmed with the designer, and he stated that this separate ground are to be fed from the substation ground, which confirm my understanding where the ground should be connected to.
However in Japan, grounding system are very different. Everything has a separate ground, meaning each a separate path to the ground via a ground electrode.
Had a discussion on this subject with a Japanese engineer, and he explained that the best method to comply with the code is for each of these separate system with separate grounding to be bonded at a common ground terminal. Sort of like you ground every individual system to a common ground terminal (the substation ground). Does it sound correct?
The contractor stated that the TVSS should NOT be connected to the substation ground, since it is a surge path, and it should be kept separate fromm the normal system ground. He stated the same thing for the isolation transformer for the IM room, which he said should have independent grounding, and not to the bldg substation.
I do not believe this satisfy the code, doesn't that make the bldg have different ground potential, at the normal substatsion ground, isolation transformer, TVSS?