jmbelectrical
Electrical
- Jul 16, 2011
- 126
A well pump equipped with a 230V, single-phase, 1.5 HP, PSC motor with a nominal full-load current of 9A is being controlled through a VFD. Upon startup of the pump, it immediately draws approximately 18A (Allegedly measured by the electrical contractor at both the line-side and the load-side of the VFD) and causes the VFD to trip on an overload condition. The VFD is supposedly rated for single-phase in, single-phase out applications.
When the VFD is bypassed through an across-the-line starter, the pump draws 9A and operates with no issues.
The VFD and the pump were specified by another consultant, so the choice to go with a single-phase configuration was out of our hands. Years ago, I recall reading that controlling a single-phase motor via a VFD was basically asking for trouble. Is that still true today?
Any thoughts on what could be going on?
Thanks, everyone!
When the VFD is bypassed through an across-the-line starter, the pump draws 9A and operates with no issues.
The VFD and the pump were specified by another consultant, so the choice to go with a single-phase configuration was out of our hands. Years ago, I recall reading that controlling a single-phase motor via a VFD was basically asking for trouble. Is that still true today?
Any thoughts on what could be going on?
Thanks, everyone!