pisimatza
Electrical
- Nov 30, 2007
- 41
Hi
IT systems are systems conected to earth through an impedance. To lower short circuit curent, right ?
I have a situation, 380 V, 50 HZ, transformer 2MVA, where i have to choose circuit breakers for an IT system, and in CB catalog , the values for "single phase breaking capacity Iit " are very low: 6, 12, 20 kA. Or max 36 kA for "strongest" MCCBs with Icw = 150 kA for 1 s. The required "short time current" is 50KA /0,5 s.
1. Are those MCCB-s suitable, or low single phase breaking capacity makes then un-usable?
2. Aditional question: in attached diagram 10 A is the maximum short circuit current value, limited with the impedance(resistance)?
3. Then why they(engineers) ask 50kA?
IT systems are systems conected to earth through an impedance. To lower short circuit curent, right ?
I have a situation, 380 V, 50 HZ, transformer 2MVA, where i have to choose circuit breakers for an IT system, and in CB catalog , the values for "single phase breaking capacity Iit " are very low: 6, 12, 20 kA. Or max 36 kA for "strongest" MCCBs with Icw = 150 kA for 1 s. The required "short time current" is 50KA /0,5 s.
1. Are those MCCB-s suitable, or low single phase breaking capacity makes then un-usable?
2. Aditional question: in attached diagram 10 A is the maximum short circuit current value, limited with the impedance(resistance)?
3. Then why they(engineers) ask 50kA?