A damaged section of an existing cable is to be removed and replaced with a new cable.
- Existing Cable: 3c, Al, XLPE/Cu screen on each core/PVC, 3.8/6.6kV
- New Cable: 3c, Al, XLPE/Cu screen on each core/SWA/PVC , 3.8/6.6kV
Two cable joins are required.
Continuity of the copper screens of each conductor will be affected by connecting each screen of the existing cable conductor to the screen of the corresponding conductor of the new cable.
At each terminating end of the existing cable, the screens of the three phase conductors will be solidly bonded and connected to earth.
At the two joints between the new cable and the existing cable, the steel wire armouring ( SWA ) of the new cable will be connected to earth electrodes.
The existing cable does not have SWA.
Question:
Should the SWA of the new cable be bonded to the screens of the existing and new conductor ?
How do MV cable joints accommodate connecting a 3c, Al, XLPE/Cu Screen on each core/PVC cable without SWA with a cable with SWA ?
Question: