I'm designing a rectangular concrete tank (aeration basin) for a wastewater treatement facility. The tank is approximately 100' feet long with circular ends. There is a free-standing wall on the inside of the tank that separates the tank into 2 - 12' wide ditches. The tank will be an above ground tank approximately 12' deep.
I'm familar with the PCA guide for the Design of Rectangular Concrete Tanks (5th Ed.)
I have designed the side walls as cantilevers using the appropriate factors discussed in the ACI codes. The walls are 12" thick with 2 layers of steel. I feel very comfortable with the design.
However, I am still confused regarding the joint layout and spacing. The design guides I've used so far don't provide much information regarding joint spacing for the main walls.
The PCA information I've found generally recommend limiting the joint spacing in the walls to about 20'-0 OC max. I have seen other similar tank wall designs where they push the joint spacing up to 50 or 60'-0...this seems excessive to me.
Generally, what is the recommended spacing or "rule of thumb" for spacing of joints both in the vertical side walls and slab?
I'm familar with the PCA guide for the Design of Rectangular Concrete Tanks (5th Ed.)
I have designed the side walls as cantilevers using the appropriate factors discussed in the ACI codes. The walls are 12" thick with 2 layers of steel. I feel very comfortable with the design.
However, I am still confused regarding the joint layout and spacing. The design guides I've used so far don't provide much information regarding joint spacing for the main walls.
The PCA information I've found generally recommend limiting the joint spacing in the walls to about 20'-0 OC max. I have seen other similar tank wall designs where they push the joint spacing up to 50 or 60'-0...this seems excessive to me.
Generally, what is the recommended spacing or "rule of thumb" for spacing of joints both in the vertical side walls and slab?