SJI recommends minimum seat welds which are routinely checked when seats must transfer external loads into the joist chords. But what about internal forces? For a building with multiple bays of joists (assume equal spans and loads) with joists on each side of the supports, the column shortening effect from the compression load in the top chord is restricted by the joist in the adjacent bay. The way I see it, if one end of the joist is not free to "slide" (it could be lateral deflection of a beam or wall), then the chord force is restrained and must be transferred at the joist seat. Has anyone else ever considered this load in determining the weld requirements for the seat? I have attached an example calculation for clarify my question. (Note that I use the full chord force to calculate the column shortening of the top chord. The chord force is really a gradient and so perhaps would be half of what I show.)