Sir,
Consider a 66/11kv transformer (star-star earthed at both side neutrals) in a solidly earthed system. Also consider one 11/0.44kv Delta/star transformer is connected to 11kv side of the 66/11kv transformer. The supply is fed from 66kv side of the 66/11kv transformer and this is stepped down to 440volts by 11/0.44kv transformer for ditribution. The 66/11kv transformer is of core type.
Suppose 'A' phase on 66kv side of the transformer became disconnected by jumper opening of the 'A' phase of the line connected to the transformer. In this situation, I think the flux due to 'B' and 'C' phase currents will flow through limb of the 'A' phase of transformer core. But in the 66kv side, there will be only two phases and the 'A' phase in the 11kv side will carry current due to the flux in 'A' phase core due to the currents in 'B' and 'C' phases in the 66kv. That is, in 11kv side there will be 3 phase currents. But the current in 66kv will increase in order to supply current in 'A' phase in 11kv side. If earth fault relay was connected in 66kv side cts, it will trip if the residual current is above pick up value due to the load in 11kv side.
Am I correct? I want to know whether my analysis is correct. Please help me with your valuable comments.
with regards,
appunni
Consider a 66/11kv transformer (star-star earthed at both side neutrals) in a solidly earthed system. Also consider one 11/0.44kv Delta/star transformer is connected to 11kv side of the 66/11kv transformer. The supply is fed from 66kv side of the 66/11kv transformer and this is stepped down to 440volts by 11/0.44kv transformer for ditribution. The 66/11kv transformer is of core type.
Suppose 'A' phase on 66kv side of the transformer became disconnected by jumper opening of the 'A' phase of the line connected to the transformer. In this situation, I think the flux due to 'B' and 'C' phase currents will flow through limb of the 'A' phase of transformer core. But in the 66kv side, there will be only two phases and the 'A' phase in the 11kv side will carry current due to the flux in 'A' phase core due to the currents in 'B' and 'C' phases in the 66kv. That is, in 11kv side there will be 3 phase currents. But the current in 66kv will increase in order to supply current in 'A' phase in 11kv side. If earth fault relay was connected in 66kv side cts, it will trip if the residual current is above pick up value due to the load in 11kv side.
Am I correct? I want to know whether my analysis is correct. Please help me with your valuable comments.