kvkev
Electrical
- Apr 12, 2002
- 16
I have a 2 element kwh meter which is reading only 20% of the expected calculated kwh value. It is connected to a 3.3 kv system via two residually connected ct's, and two vt's with a common secondary ground. I have a power analyser meter on which I have measured the input to the upper and lower elements of the meter. The ct's and vt's are outputing the correct values, but I suspect that the polarity of one or both of the ct's is wrong. How do I deduce which connections are incorrect? Can I change polarity at the meter, or do I have to do it at the ct's?
Regards,
kvkev
Regards,
kvkev