TADRICK

Electrical
Dec 8, 2006
1
Currently, I'm using a large generator and automatic transfer switch for back up power to a particular motor driven system in a location with extremely dirty / unreliable power. With this method though, the system currently requires a reset whenever the generator is switched on since the switch to backup is not immediate. To limit/eliminate these resets, I've been considering using some sort of 3-phase battery back up, but that gets pretty pricey for the size I'd need (at least 8KVA). Could I please get some recommendations so I can prevent having to constantly reset the system?
 
Replies continue below

Recommended for you

You can configure the motor control system so that it restarts automatically once the generator starts.
 
can you provide a battery backup just for the control power so it will ride through the switch over? That would be a lot cheaper and simpler if you can do it since it seems your backup generator and transfer switch is working just fine for the rest of the load.
 