Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Lateral Torsional Buckling Restraint of an Upset Wide Flange beam

Status
Not open for further replies.

msquared48

Structural
Aug 7, 2007
14,745
Anyone ever braced the top flange of a 21" deep wide flange with web stiffeners tied to wood joists? Force to develop is only 4 kips to develop at the 1/4 points using the 2% general rule and that seems doable. Only concern to me is the use of wood joists instead of steel members at the quarter points.

Mike McCann, PE, SE (WA)


 
Replies continue below

Recommended for you

Not in the direct scenario you are discussing, but I have counted wood joists framing into a steel beam as lateral bracing of the top flange. But they were connected to a nailer that was bolted to my steel beam.

provided you had a solid connection between the wood and the steel I can't see it being an issue.
 
I've done it. The trouble with wood as bracing is rarely the strength so much as the stiffness. A wood bracing member, and the wood diaphragm that holds it still, are usually a good deal less stiff than a comparable steel system normally is. As long as you check the bracing strength and stiffness using the AISC provisions, you should be fine.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 