I m at 1500 mw substation now.We try to make first fire of turbine..But during start up with LCI , I realized that currents were ot balanced for unit differential relay.
It seems B and C phases are swaped.Currents were enogh to see differential current, but I couldnt see any differential.It was Zero.
Is it because of LCI'motor effect or another something ??
THANKS.