Anyone,
34000 HP synchronous motor, two identical windings delivering half total horsepower driven by LCI drives at 2800 VAC in marine environment. One winding flashed phase to phase at the buss rings. Windings and stator cabling determined to be contaminated with salt water. Windings given superfician cleaning and the motor restarted. Flashed again at 1500 VAC. Affected half disconnected and the lead terminations insulated by shrink tubing and the motor restarted. Operated normally at low speeds and at approximately 2100 VAC, flashed over again. Buss connector rings approximately 80 MM apart and disconnected windings flashed phase to phase. The drive is fed from an ungrounded delta secondary and the Y point is grounded through 5 parallel 1600 ohm resistors. It was discovered that 4 of the 5 had been broken so that the Y ground was 1600 ohms instead of the parallel resistance of 5 of them.
Question is, could the disconnected windings have developed the 20K volts or so required to flash across the distance between the buss rings or is there something else at play here. I would think that transformer action would generate 2100 volts plus or minus and the Y resistor was designed to limit ground currents and even an increase of 5X would not generate the requisite voltage. What am I missing here? Megger, PI and surge comparison tests indicate a good winding and the low megger cables have been replaced and the motor appears to be operating normally after a two day cruise but I am concerned about transients that the OEM engineer indicated could be the problem.
34000 HP synchronous motor, two identical windings delivering half total horsepower driven by LCI drives at 2800 VAC in marine environment. One winding flashed phase to phase at the buss rings. Windings and stator cabling determined to be contaminated with salt water. Windings given superfician cleaning and the motor restarted. Flashed again at 1500 VAC. Affected half disconnected and the lead terminations insulated by shrink tubing and the motor restarted. Operated normally at low speeds and at approximately 2100 VAC, flashed over again. Buss connector rings approximately 80 MM apart and disconnected windings flashed phase to phase. The drive is fed from an ungrounded delta secondary and the Y point is grounded through 5 parallel 1600 ohm resistors. It was discovered that 4 of the 5 had been broken so that the Y ground was 1600 ohms instead of the parallel resistance of 5 of them.
Question is, could the disconnected windings have developed the 20K volts or so required to flash across the distance between the buss rings or is there something else at play here. I would think that transformer action would generate 2100 volts plus or minus and the Y resistor was designed to limit ground currents and even an increase of 5X would not generate the requisite voltage. What am I missing here? Megger, PI and surge comparison tests indicate a good winding and the low megger cables have been replaced and the motor appears to be operating normally after a two day cruise but I am concerned about transients that the OEM engineer indicated could be the problem.