For a load it is easy to figure out what lagging and leading are (inductive and capacitive). Also the terminology of vars flowing in a given direction is unambiguous. But the terminology of leading/lagging as applied to generators seems a little confusing to me. I excerpt here from the post on "Voltage Drop on Large Motor Startup"
Maak - (2) A induction motor driven above its rated speed delivers leading power factor current back into the line -- it must derive its exciting current from the line. This is a very simple form of generation of power and for certain power systems is an almost ideal method of increasing line capacity."
aolalde - (2) It should read "delivers lagging power factor current back into the line"
dpc - Actually, it is correct as written. A generator that is producing kW and absorbing kVars is leading. A generator producing kW and producing kVars is lagging. This is true for synchronous and induction machines.
aolalde - dpc: As far as I know, LEADING CURRENT is obtained from static capacitors or overexcited synchronous machines connected in parallel with the load. LAGGING CURRENT is obtained from inductances.
The power will follow the current since for a given voltage (V), P = V*I.
electricpete - fwiw - I agree with the power factor terminology as described by aolalde.
Scotty UK - Lordy, I'm going to disagree with Aolalde and ePete in one post! I'm in agreement with dpc and Maak re. generator VAr terminology: In the UK a generator exporting VAr's (over-excited) is deemed lagging, while a generator importing VAr's (under-excited) is deemed to be leading. For a load, a consumer of VAr's is deemed to be lagging (inductive) and a producer of VArs is deemed to be leading (capacitive).
What Scotty and dpc are saying is a generator has the same terminology (lagging or leading) as the load it supplies. That sort of makes sense when we consider that we restrict the power factor angle to be less than 90 degrees. If we viewed the generator and load as having opposite properties (one leading and one lagging), remembering they share the same voltage and the 180-degree opposite current, we would conclude one has power factor angle below 90 and one has power factor angle above 90 (not permitted).
Explain it to me again.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
Maak - (2) A induction motor driven above its rated speed delivers leading power factor current back into the line -- it must derive its exciting current from the line. This is a very simple form of generation of power and for certain power systems is an almost ideal method of increasing line capacity."
aolalde - (2) It should read "delivers lagging power factor current back into the line"
dpc - Actually, it is correct as written. A generator that is producing kW and absorbing kVars is leading. A generator producing kW and producing kVars is lagging. This is true for synchronous and induction machines.
aolalde - dpc: As far as I know, LEADING CURRENT is obtained from static capacitors or overexcited synchronous machines connected in parallel with the load. LAGGING CURRENT is obtained from inductances.
The power will follow the current since for a given voltage (V), P = V*I.
electricpete - fwiw - I agree with the power factor terminology as described by aolalde.
Scotty UK - Lordy, I'm going to disagree with Aolalde and ePete in one post! I'm in agreement with dpc and Maak re. generator VAr terminology: In the UK a generator exporting VAr's (over-excited) is deemed lagging, while a generator importing VAr's (under-excited) is deemed to be leading. For a load, a consumer of VAr's is deemed to be lagging (inductive) and a producer of VArs is deemed to be leading (capacitive).
What Scotty and dpc are saying is a generator has the same terminology (lagging or leading) as the load it supplies. That sort of makes sense when we consider that we restrict the power factor angle to be less than 90 degrees. If we viewed the generator and load as having opposite properties (one leading and one lagging), remembering they share the same voltage and the 180-degree opposite current, we would conclude one has power factor angle below 90 and one has power factor angle above 90 (not permitted).
Explain it to me again.
=====================================