How much leakage should be speciffied for a Rubber Gasketed
Reinforced Concrete Pipe, class B-25 , ASTM C361?
There are any standards regarding maximum laekage allowance for this kind of pipe?
Can the pipeline meet 20 gals/24 hrs/inch dia/mile?
Thanks
 
Replies continue below

Recommended for you

By the "Standard Specifications for Sewer and Water Construction in Wisconsin", Fifth Edition, Addn. No. 2, March 1, 1999, Chapter 3.7.0: "leakage test of snitary sewers" includes allowable limits of infiltration based on 200 Gal./In. Diam./Mile. Table 5:
Diam of sewer (inches) Infiltration per ft. per hr. (Gal)
4 0.0063
6 0.0095
8 0.0126
10 0.0158
12 0.0190
15 0.0237
18 0.0284
21 0.0332
24 0.0378
27 0.0426
30 0.0474
36 0.0568
42 0.0663
48 0.0758

42"diam Manhole- 0.0663 Gal per vertical ft. per hr.
48"diam Manhole- 0.0758 Gal per vertical ft. per hr.
Perhaps your State has similar limits.