Gerry123
Electrical
- Oct 4, 2012
- 2
Hi,
I have a situation to decide whether to move 3MVA 11KV/415V Outdoor transformers about 10m away from a switchroom building inorder to prevent having to build fire barriers / blast walls as required by standards if the transformers are within 7.5 m of the switchroom building.
Situation 1: 3MVA 11KV/415V TX located 10m away from switchroom and protected upstream by IDMT Relay and down stream in switchroom Over Current and Earth Fault. No Blast Walls so less capital outlay
Situation 2: 3 MVA 11KV/415V TX located 1.5m away from switchroom and protected upstream by IDMT Relay and down stream in switchroom Over Current and Earth Fault. Blast Walls required
Question is what are the impacts regarding protection of the transformer secondary or transformer secondary cables if the length to the downstream short circuit protection increases. Is there increased risk to situation 1 transformer due to the increased distance. Are there other protection configs such differential protection which may be more suitable?
Any Info appreciated. Standards I'm referring is an australian standard AS 2067 which similar to IEC standards.
Thank
Gerry
I have a situation to decide whether to move 3MVA 11KV/415V Outdoor transformers about 10m away from a switchroom building inorder to prevent having to build fire barriers / blast walls as required by standards if the transformers are within 7.5 m of the switchroom building.
Situation 1: 3MVA 11KV/415V TX located 10m away from switchroom and protected upstream by IDMT Relay and down stream in switchroom Over Current and Earth Fault. No Blast Walls so less capital outlay
Situation 2: 3 MVA 11KV/415V TX located 1.5m away from switchroom and protected upstream by IDMT Relay and down stream in switchroom Over Current and Earth Fault. Blast Walls required
Question is what are the impacts regarding protection of the transformer secondary or transformer secondary cables if the length to the downstream short circuit protection increases. Is there increased risk to situation 1 transformer due to the increased distance. Are there other protection configs such differential protection which may be more suitable?
Any Info appreciated. Standards I'm referring is an australian standard AS 2067 which similar to IEC standards.
Thank
Gerry